9/10/2008 10:04 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hi If I understood right, you want change control unit. In this situation is better to use old drawings about TI505 ( You had some drawings how is connected each sensors, valves and other staff). Just follow this drawings, disconect one by one and connect to correspond type of card. You need only S7-300 Module Specification Manual. regards |
Last edited by: UMENCHO at: 9/10/2008 10:05 AM |
|
9/10/2008 10:54 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hi Let's star with S7-300 analog input card SM331,AI(6ES7-331-1KF01-0AB0). Read this manual SM331; AI 8x12 Bit Getting Started part 1: 4 -20mA . (part 4.2, 5.2, 6.2). From old drawings you must only to define ( + ) and (-) from sensors and connect to SM331. About 6ES7-332-5HF00-0AB0 go to part 6.11 of s7-300 Module data. Must take ( + ) and ( - ) from the connector and to connect to correspond sign of sensors.( read from old drawings). Also need to assign what kind of signal you want to output from analog card. ( with Step 7 ). regards |
Last edited by: UMENCHO at: 9/10/2008 11:15 AM |
|