3/14/2024 2:58 PM | |
Joined: 5/30/2022 Last visit: 9/24/2024 Posts: 582 Rating: (96) |
Hi TheRealS1ack, 1- Do you have the correct PG/PC interface? It must be with your network card. TCPIP.1 2- Do you ping the PLC? To do that, you need to be on the same subnet 3- Have you tried another cable? 4- Try using PRONETA: PRONETA Basic 3.6 Commissioning and Diagnostics Tool for PROFINET 5- If nothing works, reset the PLC with an empty memory card: How can you use the memory card for the S7-1200 CPU? |
If this information really helps, you could use the Rate function. |
|