i faced this problem before i diidn't have the orignal software so i tried to upload it from Station but when upload HW configuration the uploaded was with default addresses, So i couldn't know the correct addresses those used in Software,, So faced problem in compileing coz the addresses in software is differents with HW ,, and can know the addresses like Digitals and Analogs by comparing,, but the big problem is with HSC and pulse generator correct addresses those assigned in HW !!! Do you have other ways to know the assgined addresses for HSC those used in Sotfware ? thanks for your advice |
Last edited by: CS Moderator at: 1/6/2013 11:13 PMnew subject after splitting from /tf/WW/en/Posts/84742#top |
|
1/31/2013 3:06 PM | |
Posts: 267 Rating: (24) |
Hello, you will find the default I/O addresses of the S7-1200 HSCs on page 344: http://support.automation.siemens.com/WW/view/en/36932465 You must have a look in the program code if the project author has changed this or adjust it by your own. |