7/22/2013 6:15 PM | |
Joined: 7/8/2009 Last visit: 8/5/2024 Posts: 1976 Rating: (477)
|
You have to set P10 -30, then P970 to 1 for factory reset Please refer Manual for more Parameter List: MICROMASTER 440 Operating Instructions: MICROMASTER 440 0,12 kW - 250 kW Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/24/2013 10:02 AM | |
Joined: 7/8/2009 Last visit: 8/5/2024 Posts: 1976 Rating: (477)
|
I once again have to say that please use search function on top right corner This is very common fault and discussed lot of time here, i am sure you will get it solved by reading those discussion here is what i got by just typing f022 https://support.automation.siemens.com/WW/llisapi.dll?query=f022&func=cslib.cssearch&content=adsearch%2Fadsearch.aspx%3Ftab%3D2&lang=en&siteid=csius&objaction=cssearch&searchinprim=_searchinprim_&nodeid=99&x=16&y=8&cssearchengine=NEW Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
This contribution was helpful to1 thankful Users |
7/31/2013 7:07 AM | |
Posts: 241 Rating: (50) |
I've same problem too... I've checked r0947 = 22 and r0949 = 1 How could I checked the IGBT??? So,when this happen,can inverter fixed without repairing??? Thank you it means " DC link overcurrent condition = IGBT short-circuit " you can check it by cold testing procedure. Check attachment to test IGBT If IGBTs are faulty then it has to be repaired.. AttachmentIGBT Testing.zip (665 Downloads) |
9/23/2021 8:42 AM | |
Joined: 5/28/2008 Last visit: 10/4/2024 Posts: 4515 Rating: (839)
|
Hi, Please follow bellow instructions |
Ayman Elotaify |
|