1/16/2022 9:05 PM | |
Joined: 9/27/2006 Last visit: 11/6/2024 Posts: 12293 Rating: (2690) |
Hello ISD_ENG; Have a look at these extracts from the ComProfibus v5.1 manual, see the screenshot below. Once you have placed the new gsd file in the correct directory (with all the existng gsd files), you must open the File menu and command "Read in GSD Files". Only then will the Profibus slave catalog be updated. Here is a link to the ComProfibus manual: https://support.industry.siemens.com/cs/ww/en/view/1498610 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 01/16/2022 21:05:53 |
|
1/17/2022 8:41 PM | |
Joined: 1/16/2022 Last visit: 9/30/2024 Posts: 9 Rating: (0) |
Hi KSN, I have checked it in Slave and it's all subfolder but there wasn't. Thank you. |
1/18/2022 5:36 AM | |
Joined: 8/25/2006 Last visit: 11/6/2024 Posts: 2211 Rating: (280)
|
Hello. To which folder did you copy gsd-file? It should be C:\SIEMENS\CPBV51\gsd. May be your gsd-file is corrupted. Try attached gsd-files, unzip them before copying. There are 2 files: DPV0 and DPV1. AttachmentRPBA-01.zip (861 Downloads) |
This contribution was helpful to1 thankful Users |
2/6/2022 12:39 AM | |
Joined: 1/16/2022 Last visit: 9/30/2024 Posts: 9 Rating: (0) |
Thank you KSN, it's done. |
This contribution was helpful to1 thankful Users |
Follow us on