Good day all, I am having an issue with an MXL system. I had to replace the main board due to loop 2 quit working. I was able to install the original program. I found that there was a pull station mounted on loop 2 that was "shorted" according to the hand programmer and I replaced it after matching the address to what was missing but now I am showing to have 6 devices all in that same room offline? They all have voltage and I have a more unique problem. When I take the original device to the panel and mount it on the SLC with both of loop 2 address 5 the panel shows duplicate address? The voltage to the remote building is bouncing between 19 and 22 volts, what is the amp draw supposed to be on a system ran thru 140 feet of cable on MXL? Any feedback would greatly help me. Thanks, David ------------------------------------------------------------------------------------------ |