Hi. We are planning to integrate a SIEMENS 9610 Power Meter to our SCADA System. Now, we have it integrated to our system using Modbus TCP. And we plan to integrate it using IEC 61850. We have been trying to get the ICD file from the meter itself, without any result. We tryed with ION Setup 3.0 And it reports "missing CID file" We also tryied with IED Scout, a browse operation over the Power meter, and reports "Server not found" What can we do? Should we consider a Firmware upgrade? Thanks a lot! ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/24/2023 11:20:28New subject after splitting |
|
7/27/2023 4:33 AM | |
Joined: 7/24/2023 Last visit: 10/1/2023 Posts: 3 Rating: (1) |
ION Setup V3.2 Schneider Electric version used. User: supervisor Password: 0 In the case of the device that we want to connect is the Access 9610 Siemens Example IP 192.168.1.XX Mask 255.255.0.0 When communication is OK this dialog appears We access the ION Setup V3.2 application, we stop on the right side of the menu inSetup Assistantand click In the Setup Assistant menu, we look for the folderCommunications/ 3rd Party Protocols / IEC 61850
We perform the following steps to convert a file ICD to CID, this file can be found in the following path:https://www.se.com/us/en/product-range/1460-powerlogic-ion7550-ion7650-series/#software-and-firmware Open the CET850 application which is an IEC6850 configurator
18. In case you are not sure how this procedure is performed, watch the following video Watch "How to Enable IEC 61850 Functionality on Your Meter" in YouTube https://youtu.be/gPYb_8k6LkU
|
Last edited by: edwardtrivino at: 07/27/2023 04:37:49Last edited by: Jen_Moderator at: 07/27/2023 11:10:31Video embedded. |
|