Dear sir, You are correct.We can use SFC14 & SFC15 to read write the data & i thinnk it will use while drive with plc is on profibus communication. What can we do in case of profinet communication? In my case s120 with S7-400 plc is on profinet communication with step7 simatic manager. Please guide in my case also. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/27/2023 10:02:06New subject after splitting |
|
1/9/2024 4:03 PM | |
Joined: 4/24/2008 Last visit: 8/2/2024 Posts: 213 Rating: (16) |
You can use the FB 283 to read it out. https://support.industry.siemens.com/cs/ww/de/view/25166781 |
|
|