1/21/2020 12:11 PM | |
Joined: 5/6/2010 Last visit: 9/12/2025 Posts: 2031 Rating:
Hello, you can connect the output of your sensor with the I+ of the module e.g. channel 0 = I+ = Pin 1 Please look at the manual for the 6ES7134-6GF00-0AA1 regards |
4/11/2024 11:45 AM | |
Joined: 8/7/2022 Last visit: 3/31/2025 Posts: 1 Rating:
Ok. So I+ to CH0 connected to Active transmistter +24VDC But what about the other wire from the transmitter? 0V? Thanks. |
4/11/2024 3:13 PM | |
Joined: 3/28/2010 Last visit: 9/12/2025 Posts: 1172 Rating:
nA terminal for signal (-) |
4/14/2024 4:06 AM | |
Joined: 2/28/2023 Last visit: 8/22/2025 Posts: 45 Rating:
Hi Mate, Please find the 2-wire connection diagram attached However, note that the terminal connection depends on the type of 2-wire sensors either a Sink or Source type and the load is connected to the output lead that sources or sinks the conventional current. Since the conventional current flows from positive to negative of the senor, therefore, Source Type Sensor: The load terminal is connected to the negative. Sink Type Sensor: The load terminal is connected to the positive. ------------------------------------------------------------------------------------------------------Rate if resourceful Please. Attachment2-Wire Connection.pdf (705 Downloads) |