Hello, The line power adapter is a simple 120:230VACsingle phase transformer. The problem is the off the shelf 5 or 10kW SLM will not accept this supply. The factory that makes the S120 two axis demo performs internal changes on the line module to allow the demo to work off this supply (part of reason for expense). My recommendation is to bite the bullet and purchase the Siemens demo unless you have a 3-phase supply in your lab. If you have a 3-phase 230VAC supply I would use the 16kW SLM or 20kW BLM. If you have a 3-phase 460VAC supply the 5 or 10kW SLM is fine. The latest Motor Modules will work off the DC supply of 300VDC or 600VDC. AttachmentPages from d21-1_2006_e4.pdf (458 Downloads) |