3/23/2010 12:11 PM | |
Posts: 21 Rating: (4) |
Hi, [schnippschnapp] The CPU will go to run after a program update via memory cardas long as you set the Device Configuration correctly.You should set the startup parameter to "Warm Restart - RUN". Please see section 3.4 of the system manual. It describes how to handle Simatic MC's. I hope this helps, System Manual for S7-1200 is here: http://support.automation.siemens.com/WW/view/en/36932465 |
Last edited by: O_Moderator at: 3/24/2010 11:09 AM |
|