Joined: 1/23/2009 Last visit: 7/20/2024 Posts: 29 Rating: (10) |
Hi all, I connect my PAC3200 with WinCC flexible according to the instructions in attachment. Everything is working properly, but I do not know the address of other memory locations, where PAC3200 stores power factor, active or reactive power etc. I know only address of 3 memory locations: - MW1 = Voltage (UPH-N L1) - MW3 = Voltage (UPH-N L2) - MW5 = Voltage (UPH-N L3) If anyone knows the addresses of all other parameters, I would be very grateful to him Best regards Gaspar AttachmentPAC3200 and WinCC flexible.pdf (668 Downloads) |
Be creative while inventing ideas and be disciplined while implementing them... :) |
|
9/4/2010 2:06 PM | |
Joined: 10/7/2005 Last visit: 10/4/2024 Posts: 3024 Rating: (1054) |
Hello gaspar1 you'll find the addresses of all the other values in the Modbus values table chapter 3.9.3 ofTHIS PAC 3200 manual. Note the "offset" column which gives you the WinCC flexible "%MW" address (e.g. Power factor ahas an offset of 37 so you'd configure "%MW37" as the address in WinCC flexiblefor it). I hope this helps |
Cheers |
|