4/5/2012 11:16 AM | |
Posts: 8 Rating:
|
Simoreg fault F030,panel display: ...too small .check current normal-> not overload. U580 set=7.Help me answer question Why?thank |
4/5/2012 11:35 AM | |
Joined: 8/25/2006 Last visit: 9/12/2025 Posts: 2218 Rating:
|
Hello. Try to set U580=4 as suggested here: 6RA70, SIMOREG DC Master; Unwarranted F030 with fault value 2 |
Follow us on