4/15/2015 10:34 AM | |
Posts: 7 Rating:
Hi, We have a query on S7 300 Modbus TCP/IP communication. System Overview • CPU 317 PN/DP (inbuilt PN port used) is configured as Modbus TCP/IP client and the MOXA gateways – 2 nos. connected as modbus TCP server through SCALANCE switch. • Each MOXA gateway has 4 serial RS 485 interfaces & 1 ethernet interface (modbus TCP/IP). Each serial interface connected to a serial loop to the Power monitoring units. On each serial loop max 25 slave devices are connected. Similarly are total 8 serial loops connected to both gateways. • There are 2 connections (gateway - 01 & 02) configured in Modbus DB PARAM. • In user program the logic is made to poll the slave devices one by one under connection-01 & 02 • The system architecture enclosed for reference Present Scenario • Using CONTROL DAT DB we are moving the connection ID, unit ID, DB No, Start address & Length • Under Connection-01 the modbus loop devices are communicating fine. • While switching over to connection-02 (i.e. Connection ID = 2), the data transfer not happening and the status showing that connection establishment remians "True" and there is no error. Please clarify to resolve this. Thanks, Dina Attachmentscan53.pdf (713 Downloads) |
8/15/2016 9:43 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4759 Rating:
New question published by e_skazem is split to a separate thread with the subject Convert Modbus TCP to Modbus RTU, FB108want a reg_key. Best regards |
