12/20/2016 3:02 PM | |
Joined: 9/27/2006 Last visit: 8/6/2024 Posts: 12273 Rating:
Hello Roeland; Not only is it mandatory to have an option board to use Profibus on your analyser, you must also decide whther that option board will open communications to Profibus-DP or Profibus-PA. Have a look at the following document; OXYMAT 6 - Interface PROFIBUS DP/PA https://support.industry.siemens.com/cs/fr/en/view/7618463 TheA5E00015899Exi optional module allows intrinsically safe coupling to PROFIBUS-PA. TheA5E00034504 optional module allows non-intrinsically safe coupling to PROFIBUS-PA. TheA5E00019145 optional module allows coupling to PROFIBUS-DP. If you need further information on the variants of Profibus, you can search here on the forum (use the Search Box at the top right of this page) or on Profibus.com/download. But the basic difference is this: - Profibus-DP is designed for fast master-slave cyclic exchanges. Once the parameters of the communications are established, you receive continuoulsy the same process data and diagnostics from the slave. -Profibus-PA is slower, designed to integrate instrumentation in the PLC; you can not only receive the process data from the instrument, but you can also configure, calibrate and parametrise it , using an add-on software known as PDM (search on the forum for more info). Hope this helps, Daniel Chartier |
3/13/2017 5:22 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4769 Rating:
New question published by VBVBVBVBVBVBVBVBVBVBVBVBVBVBVB is split to a separate thread with the subject Read variable data from oxymate 61 on s7 1241 dc/dc/rly via CM 1214/RS485. Best regards |