12/24/2009 12:58 AM | |
Joined: 6/4/2008 Last visit: 10/4/2024 Posts: 1497 Rating: (324) |
Hi, are you using a BOP or AOP panel. You mention there is a fault showing, what is the fault? If the display on the BOP/AOP is not functioning, try another panel, try an online connection with the PC kit, or alternatively, remove the panel and see what the two LED's are doing, compare with the attached to try and work out what is happening. Also, if possible, check that the following parameters are set (These might have been changed by plugging a different operator panel onto the drive) P2010 = 6 P2011 = 0 P2012 = 2 P2013 = 127 Graeme
AttachmentLED Diagnostics.pdf (916 Downloads) |
Last edited by: Graeme at: 12/24/2009 1:22 AM |
|
12/29/2009 3:11 PM | |
Posts: 5 Rating: (1) |
Dear Sir, There is some hardware failure in VFD. Please contact Siemens service person or send your VFD to Siemens for repair/service. Regards Mukesh |
1/7/2010 3:32 PM | |
Posts: 739 Rating: (55)
|
This message indicates that the AOP has failed to communicate with the inverter that it is connected to. Pressing 'P' will acknowledge the fault and the AOP will resume normal operation. Possible causes of communications problems include damaged wires or a poor connection to the inverter. see also FAQ: http://support.automation.siemens.com/WW/view/en/30363159 |
This contribution was helpful to1 thankful Users |
1/25/2012 4:27 PM | |
Posts: 4 Rating: (0) |
Dear Manishkools can you specify wich parts of the VFD that you have notice the defective capacitor ? thanks |