Comm_Load block |
6/14/2022 2:24 PM | |
Joined: 11/12/2017 Last visit: 2/16/2023 Posts: 14 Rating: (0) |
And the COM16 Modbus interface |
6/15/2022 1:17 PM | |
Joined: 4/8/2021 Last visit: 10/31/2024 Posts: 639 Rating: (107) |
Hi, Depending on the application, the information at the "STATUS" parameter is only available for the duration of one cycle. Since the CPUs work in the millisecond range, the information cannot always be noticed by the user. Maybe you are not seeing STATUS values because of that. I suggest you to follow the following FAQ in order to be able to see real values of STATUS parameter. https://support.industry.siemens.com/cs/ww/en/view/109745539 By the way, to my knowledge, is not a "good practice" to set clock marks to MB_MASTER REQ input. For test it, at the beggining, i would do request manually. Hope it helps. Br, Cocolino |