Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015) |
Hi, sorry but the PAC3200 you used have no PROFIBUS and no PROFINET Interface so you can't get a GSD or GSDML File for this device. look in the Application examples if you can find a way to use the PAC3200 in you config: https://support.industry.siemens.com/cs/ww/en/ps/7KM2111-1BA00-3AA0/ae Regards Christoph |
This contribution was helpful to1 thankful Users |
11/10/2015 3:23 PM | |
Posts: 15 Rating: (0) |
Hi again and thanks for reply. I am sending you photos of my PAC3200 and PLC S7-1500. My project is to display values from PAC on PLC's screen (e.g. Voltage). What is the best way to establish connection with my configuration? Attachmentphotos.rar (624 Downloads) |
11/10/2015 3:45 PM | |
Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015) |
Hi, I found only the FW V3.0.5 in the support (https://support.industry.siemens.com/cs/ww/en/view/45148103) the Version V3.0.3 from you screen i can't find , can the problem solved with a FW Update of the DP Module?
Christoph |