5/25/2009 10:10 AM | |
Posts: 17 Rating:
|
Hello, I am waiting for your reply. Regards Kristine |
5/25/2009 2:40 PM | |
Joined: 10/3/2008 Last visit: 9/8/2025 Posts: 996 Rating:
|
Hi kristine, you parameterize the register 640 (dez) as the first register in DB14, but then you want to write the register 0 (START_ADDRESS = 0). So it's clear, that this errorcode occurs. If you want to use the configuration start_5 = 640 (dez), then the START_ADDRESS has to be 640 (dez) at least. If you want to write the START_ADDRESS = 0, then you have to change the initialization start_5 = 0. You can read or write only these addresses, which you have parameterized in OB100. Wüstenräuber |
5/25/2009 2:57 PM | |
Posts: 17 Rating:
|
hi tried as you said L 640 L 2 SET |
Last edited by: kristine at: 5/25/2009 5:32 PM |
|
5/25/2009 5:51 PM | |
Joined: 10/3/2008 Last visit: 9/8/2025 Posts: 996 Rating:
|
Hi kristine,
Wüstenräuber |
5/25/2009 6:17 PM | |
Posts: 17 Rating:
|
Here is the new project
AttachmentTestny.zip (624 Downloads) |
Last edited by: kristine at: 5/25/2009 6:20 PM |
|
5/25/2009 7:40 PM | |
Joined: 10/3/2008 Last visit: 9/8/2025 Posts: 996 Rating:
|
This DB is not the online DB from your CPU. The whole parameters are set to the default value. Try again: Download the blocks to the CPU, set CPU to RUN and start an order with ENQ_ENR = TRUE. After that go to online view in SIMATIC Manager and copy this online DB. Wüstenräuber |
5/25/2009 7:51 PM | |
Posts: 17 Rating:
|
Hello, Here it is once again,i hope this is the right one now;) Regards Kristine AttachmentTestny.zip (635 Downloads) |
Follow us on