My plan is to use the ladder logic and the PLC to control multiple components (compressor, solenoids, etc.) I wanted to use the HMI as both a display for various analog inputs connected to the PLC, throw alarms, and set certain outputs for the PLC. The ladder logic is finished, setting up the link between LOGO tags and HMI tags is where I am stuck. The zipped files are attached, thanks.
AttachmentHMI Controls.zip (586 Downloads) |
8/18/2022 10:21 PM | |
Joined: 12/18/2014 Last visit: 9/26/2024 Posts: 33838 Rating: (4205) |
I asked you to describe what data you want to exchange. You then reply with a general answer. |
8/19/2022 3:15 AM | |
Joined: 12/18/2014 Last visit: 9/26/2024 Posts: 33838 Rating: (4205) |
In attachment a little example. You must use the VM area of the LOGO!. You can't read or write the analog values in the HMI as IW (Input word). Take a look at Parameter-VM-Mapping in the LOGO! program. AttachmentDangeruss24.zip (667 Downloads) |