I understand your problem! You are just changing the slave id/unit but you have to change the port number on the same IP. ie: 10.10.20.30:502 is your main PAC-4200 access and 10.10.20.30:17002 to access Slave-1 if the RS485 bus is connected to the "MOD1" slot. here is the official document link: https://support.industry.siemens.com/cs/attachments/34261595/manual_pac4200_en-US_en-US.pdf?download=true see the page number: 41 Although it's too late to answer but it may help someone! Thanks, Aman Attachmentmanual_pac4200_en-US_en-US.pdf (576 Downloads) |