2/2/2016 11:58 AM | |
Posts: 31 Rating: (0) |
Hello to all, I am working on pedal robot. my system is consist of: sinamics s110 with CU305. my problem is related to the fault 7930. when I wanted to run from control panel, I got one error which says:the switch-on disable of the drive is actve and in the Alarm tab, it gies me the fault : 7930 Drive:Brake control error(10). also on the Bop 20 which is installed in my system there is this Fault. please help me. I am waiting for your kindly help regards ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 2/2/2016 3:39:22 PMNew subject after splitting |
|
2/2/2016 5:42 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980)
|
Hello, for the motor holding brake you need a Brake Relay, this is connected to the PM340 and then to the motorbrake. The Module is described in the Device Manual Capter 7.5 Regards Christoph |
2/5/2016 3:47 AM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980)
|
Hello, yes in this case you must buy the brake control relay to control the Motor Holding brake.
Christoph |