10/3/2011 9:09 AM | |
Joined: 5/27/2008 Last visit: 11/17/2024 Posts: 29 Rating: (0) |
Are you sure that the "service mode" of the FTC card was active? Otherwise the card will not accept the calibration. |
10/3/2011 10:31 AM | |
Posts: 74 Rating: (0) |
Thank you for the reply yes i am sure check the attached picture |
10/4/2011 1:40 PM | |
Joined: 1/4/2007 Last visit: 11/13/2024 Posts: 1147 Rating: (175)
|
Hello Palestine, Maybe the adjustment digits “adjustment digits for zero” and “adjustment digits 1” are too close together. I can help you more if you can send to me a Siwatool file (see the attached file please) with the current parameter settings of the FTC module after the error occurred. Best regards Siwarexi Attachmentcreate_a_SIWATOOL-file.pdf (376 Downloads) |
10/5/2011 7:20 AM | |
Posts: 74 Rating: (0) |
Thank Siwarexi here is the .ftc file for the siwarex AttachmentSIWAREX_Settings.zip (333 Downloads) |
Last edited by: Palestine at: 10/5/2011 7:26 AM |
|
Follow us on