12/15/2008 1:31 PM | |
Posts: 217 Rating:
|
Dear Jamil, 1) Yes it can happen please go to process value DR30 and check the ADC before filtering and after filtering. The value of ADC is the current value of process. To adjust zero use the process value with out load to “Adj. Digit 0” in calibration screen. 2) No actually an Adj weight 2 is for calibrating for a second calibration. 3,4) See the attachments. I think this will help you. Thanks AttachmentDoc1.pdf (716 Downloads) |
12/16/2008 1:42 PM | |
Joined: 1/4/2007 Last visit: 8/26/2025 Posts: 1190 Rating:
|
Hello, To your questions: 1) + 2) At first, you need to calibrate your scale, because each scale has different load cells, dead load, and so on. Into the internet, you can see the procedure, how to do a calibration with the Siwarex MS module, with the following link: http://support.automation.siemens.com/WW/view/de/26624348 3) +4) Into the manual of the Siwarex MS module, you can see into the chapter 8 the programming into Step7. Especially the chapter: - 8.9.1 shows you how to tare the scale via Step7 - 8.9.2 shows you how to read and write data from/to the Siwarex MS module via Step7. You can find the manual into the internet with the following link: http://support.automation.siemens.com/WW/view/en/22600601 Best regards |
Last edited by: Siwarexi at: 12/16/2008 1:47 PM |
|
1/5/2009 6:44 AM | |
Posts: 217 Rating:
|
Hi, I think you should calibrate the siwarx module. To my knowledge the tare weight is retentive it’s a module’s feature. For basic load cell application the additional library is not needed. Actually it is a subroutine as if you see the sample project. If you need you can use it as a library or as it is. If you are using HMI additinal block will help you a lot.(juest to modify the sample projct as for you requirement See this two links also from that you can down load a sample program. There you can find additional subroutine. https://support.automation.siemens.com/WW/skm/frameset.asp? url=%2FWW%2Fllisapi%2Edll%2F22605342%3Ffunc%3Dll%26objId% 3D22605342%26objaction%3Dcsopen%26skm%3D1%26lang%3Den&Query= siwaerx+ms&SearchArea=downl&id=22605342&F11Marker=true&siteid=cseus https://support.automation.siemens.com/ WW/skm/frameset.asp?url=%2FWW%2Fllisapi%2Edll %2F28309818%3Ffunc%3Dll%26objId%3D28309818%26objaction %3Dcsopen%26skm%3D1%26lang%3Den&Query=siwaerx+ms&SearchArea= downl&id=28309818&F11Marker=true&siteid=cseus&query2=&modelled=&lang=en For the quick question, yes you can get zero that way. Also you can do that form siwa tool’s service adjustment tab, click adjustment zero valid. See the attachment. I hope this will help you. |
1/7/2009 12:27 PM | |
Posts: 217 Rating:
|
Dear jamil, Your first step is correct. But for second step and 3rd step please read this attachment. Regards. AttachmentResolution of SIWAREX MS.zip (586 Downloads) |
1/13/2009 2:45 PM | |
Joined: 1/4/2007 Last visit: 8/26/2025 Posts: 1190 Rating:
|
Hello, I would like to give you some information to the Siwarex MS module: 1) Into the internet, you can see the procedure, how to do a calibration with the Siwarex MS module, with the following link: http://support.automation.siemens.com/WW/view/de/26624348 I also attached a short file for you with the minimum settings into Siwatool for a calibration. 2) The tare-command is not retentive! If you want to have the tare-command retentive, you have to execute the command “2” after executing the tare-command.3) You can download the library “Microscale_additional” from the internet: http://support.automation.siemens.com/WW/view/en/30347016 The current library “Microscale_V20” is only available at the configuration package CD. 4) There was a development since 04/2006: With the library “Microscale_V20” and the library “Microscale_additional” it is now possible to read/write datarecords from/to the Siwarex MS module.Best regards Attachmentadjustment_SIWAREX_MS_Siwatool_en.pdf (642 Downloads) |
This contribution was helpful to
2 thankful Users |