9/12/2014 9:04 AM | |
Posts: 4 Rating: (0) |
Hello, AttachmentD:\Temp\Back-up 3VL-MCB, MCB-MCB.pdf (780 Downloads) |
Last edited by: Min_Moderator at: 9/12/2014 12:04 PMEdit attachment path |
|
This contribution was helpful to2 thankful Users |
9/13/2014 8:45 AM | |
Posts: 6 Rating: (0) |
thanks a lot Eray Can, this is exactly what i was looking for. |
9/15/2014 10:43 AM | |
Posts: 4 Rating: (0) |
Hello, I also send selectivity tables for many protective devices. With best regards. AttachmentD:\Temp\Selectivity limits.zip (528 Downloads) |
Last edited by: Min_Moderator at: 9/15/2014 4:11 PMChange attachment name |
|
9/17/2014 8:17 AM | |
Posts: 6 Rating: (0) |
This is exactly what I need. Thank you Eray Can! |
8/23/2016 10:32 AM | |
Posts: 4 Rating: (0) |
Hello, In the "Back-up 3VL-MCB, MCB-MCB.pdf" file there are Back-up values tables. In the "Selectivity limits.xls" file there are Selectivity limits values. For 3VL4 ETU 10 and 5SY4 selectivity, I have also found old 2006 deutsch brochure (in attachment), which selectivity values are very close to excel file. Hope hepls. AttachmentSelektivität DE 2006.pdf (363 Downloads) |
9/20/2017 3:18 PM | |
Posts: 4 Rating: (0) |
Hello, You can find "Low Voltage Protection Devices Selectivity-Tables" at below link. Hope hepls. |
3/15/2018 11:25 AM | |
Joined: 6/19/2017 Last visit: 5/22/2024 Posts: 8068 Rating: (164) |
New question published by borlaboy is split to a separate thread with the subject Need tables with specific types of 3VT/5SY and Ik limit values (Isel) for achieved selectivity. Best regards |
My Forum is the place to personalize your profile, |
|