3/11/2024 1:11 PM | |
Joined: 9/8/2011 Last visit: 4/24/2024 Posts: 527 Rating: (84) |
IN THE US: You can use Dual Circuit Safety (DCS). Special safety rated relay's. ESTOP mushrooms that require a mechanical reset (and estop labeling) to stop the CRUSHER from running. https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10143262# OR Safety PLC. Which requires 2 CPU's to monitor Circuits for Safe operation. When circuit is open - check that DCS is not shorted. When closed, they come on together (within ms of each other). Order a safe PLC, and as many inputs as you need. and as many outputs as needed. DO NOT USE NORMAL INPUTS OR OUTPUTS FOR SAFETY. BOTH of these methods require dual circuit wiring. Actual requirements depend on two main factors. "Industry Standard Practice" is the legal phrase that matters. Severity of the offending danger. Frequency of the offending danger. GOOGLE "Risk Assessment" . Some problems can be mitigated by a barrier. Depending on access requirements, some problems can use a light barrier. The short answer is yes. |
A smart person learns from their mistakes |