Chers tous, Je travaille sur un projet avec un processeur 1513. J'ai obtenu cette erreur lors du diagnostic. Erreur temporaire du processeur 3 of 23; Event ID: 16# 02:2524 Internal address details: Caddr=16#00000051, area: Area 00, addr: 0 Incoming event ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 07/15/2025 10:55:58New subject after splitting |
|
7/16/2025 6:33 AM | |
Joined: 7/31/2020 Last visit: 9/12/2025 Posts: 87 Rating:
|
Hello, If the CPU is in stop mode, you can go online under "Online & Diagnostics" > diagnostics > diagnostic buffer for this entry to "Open in editor" and come to the affected line. You can also use the call hierarchy to see from where the affected block was called. How can you determine the programming error in stop mode of the S7-1500 CPU? Regards |