8/1/2025 5:54 AM | |
Joined: 2/15/2025 Last visit: 8/1/2025 Posts: 12 Rating:
|
Thanks for information and support ! |
8/1/2025 6:44 AM | |
Joined: 9/23/2005 Last visit: 9/12/2025 Posts: 5116 Rating:
|
I'll repeat - a FW downgrade. And yes, this is a link. BTW, I'd go for FW 4.6.1 as it seems FW 4.6 has some flaws.
|
Regards, |
|
8/1/2025 8:40 AM | |
Joined: 3/30/2020 Last visit: 9/12/2025 Posts: 5446 Rating:
|
I have recently used a FW:V4.7 for a program developed in Step7 V15.1 as if a FW:V4.3. I did not have any issues. So your problem is a surprise to me. The official FAQ from Siemens does not mention FW:V4.7 explicitly. But there may be details that could be helpful. [LINK: How do you load a project into an S7-1200 CPU if its firmware version cannot be selected in the hardware catalog of STEP 7 (TIA Portal)?] What my friend Jacek mentions is very valid, even if it is not mentioned in the FAQ. There is a possible hic-up however. At some stage, a range of S7-1200 processors (some hardware build) could not downgrade; only upgrade was possible. It was a PLC with FW:V4.2 preloaded, if I recall correctly. There is a 90% chance that you will not have an issue with following what Jacek suggests. |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|