1/19/2016 4:38 PM | |
Joined: 11/17/2010 Last visit: 9/12/2024 Posts: 216 Rating:
Hi, According to the documentation attached, there is a maximum range of 2046 units and not 1024. Be careful, you have to use special bloc RLG.AA to extract value from the Analog word "Qw". Regards. AttachmentS95U-Analog value processing.pdf (899 Downloads) |
1/19/2016 5:09 PM | |
Joined: 9/27/2006 Last visit: 9/18/2025 Posts: 12413 Rating:
Hello Prassanna; The S7 analog input moduleshave their own logic that is different from their S5 equivalent(as you point out they will all use a numerical range 0-27648 or ±26748), and there are special functions (FC 105 "Scale" and FC 106 "Unscale") that are available in Step 7 to bring the analog values to (and from) engineering values. I suggest you simply reprogram them directly in the S7 project, without attempting to convert them. You will save much time and energy that way. See the following FAQ, for starters, and look at section 9.1 of the From S5 to S7 manual (on analog signal processing in the S7 PLCs): How and for which analog measurements can you use the function FC105 'SCALE' to convert the integer values (INT) into real number values? https://support.industry.siemens.com/cs/ww/en/view/1765297
This application example shows how to manipulate an analog input (from a pressure transmitter) and scale it usinmg FC 105. It might give you hints for your own project. S7-300/400 CPUs: Pressure Measurement in the S7-CPU Using SITRANS P Transmitter https://support.industry.siemens.com/cs/ww/en/view/23642357
Hope this helps, Daniel Chartier |
1/19/2016 5:12 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
Hello sorry but our friend Prassanna speaks of Analog Output and not Input, if i read the manual for S5 Analog output OnBoard, Table 12-13 on page 12-10 i read 1024 and not 2048, there is an error? S5-90U/S5-95U Programmable Controller System Manual - Siemens |
Last edited by: Ste39 at: 1/19/2016 5:13:27 PMLast edited by: Ste39 at: 1/19/2016 5:23:29 PM |
12/26/2017 8:02 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8171 Rating:
New question published by MedRamy is split to a separate thread with the subject Analog output 4-20mA instead of 0-10v which is linked with the Pin14. Best regards |