6/25/2012 8:27 AM | |
Joined: 11/18/2009 Last visit: 5/24/2025 Posts: 263 Rating:
|
Have you tried SCL Validator? http://scl-validator.erlm.siemens.de/validator/upload.html |
3/13/2013 8:15 PM | |
Posts: 3 Rating:
|
Hello all, I am trying to communicate Siemens 7sj80 and ABB RTU in vertical 61850 communication.However, I could not get any document in Siemens Relay Manual. So I read your comments. Firstly, I opened DİGSİ Configurator and 61850 System configurator and created static Report application and deleted GOOSE application just for 7SJ80. this is xx.cid does not contain any RTU file. then I exported xx.cid file of DIGSI 61850 System Configurator to the iet600 (ABB 61850 Configurator). Then I combined ABB RTU and Siemens Relay 7sj80 successfully in iet 600. Then I imported xx.scd file to the DIGSI configurator but it gives me warning like "The device 'AA1TH1' does not exist in the accepting station " on the other hand I import in RTU 560 successfully. So I downloaded files both RTU and Relay lastly. But communication was unsuccessful. So what am I doing wrong ? could you assist me? Respectfully AttachmentabbSIEMENS.pdf (1410 Downloads) |
Last edited by: evanecan at: 3/13/2013 8:56 PM |
|
3/15/2013 12:12 PM | |
Posts: 3 Rating:
|
Thank you very much. It works nicely. I tested for analog values and continue to testing. |
2/17/2024 11:33 AM | |
Posts: 1 Rating:
|
hi i am trying to configure ABB numerical realys in IEC61850 protocol with sicam scc i am doing it for first and i don't know how |