(0)| 7/6/2022 2:44 PM | |
|
Joined: 7/9/2015 Last visit: 10/30/2025 Posts: 4470 Rating:
|
Hi, please check this FAQ-perhaps it also helps you with you V90 drive: SINAMICS: Message A30042 "Fan has reached its maximum operating hours"Regards, Towome |
|
|
|
| 7/7/2022 3:42 PM | |
|
Joined: 10/11/2006 Last visit: 10/30/2025 Posts: 6047 Rating:
|
Dear fer2.0 the V90 PTIs manual describes what to do in case of alarm 30042. -Replace the fan unit by a new one -Reset p0251 onto 0 Here is the Link to the V90PTIs manual: |
|
With best regards, |
|
| 1/18/2024 2:12 PM | |
|
Joined: 10/11/2006 Last visit: 10/30/2025 Posts: 6047 Rating:
|
Hello, you have to upgrade the firmware of the drive. Description and download: https://support.industry.siemens.com/cs/ww/en/view/109746210 |
|
With best regards, |
|
| 7/12/2024 8:18 AM | |
|
Joined: 9/16/2016 Last visit: 10/28/2025 Posts: 4 Rating:
|
Thx. Regards, Alin |