8/5/2024 5:06 PM | |
Joined: 6/12/2024 Last visit: 8/12/2024 Posts: 2 Rating: (0) |
Hello, I have a project with an S210 drive and an absolute encoder. Catalog number is 1FT2204-6AF11-1Cxx. The PLC is an S7 1500 v3.0, and the drive has been updated to FW v6.3. The motion control has been configured with the positioning axis Technology Object. The drive loses the actual position of the motor during a power cycle or communications failure with the drive. Homing is performed with MC_Home Mode 7. I have noticed that the actual encoder online value (Gx_Xist1) Does not retain through the power cycle. Also if a mode 7 home is performed, and the motor is not moved from the homed position, the actual position will be retained through the power cycle. AttachmentS210 Encoder Config - Google Docs.pdf (303 Downloads) |
8/19/2024 8:35 AM | |
Joined: 7/20/2024 Last visit: 9/9/2024 Posts: 12 Rating: (0) |
Hello, no, the problem is not solved, what about you? |
8/26/2024 12:33 PM | |
Posts: 50 Rating: (4)
|
Hello, sorry for the late response. I had another look into the document. Your increments per revolution are too high. For a multiturn encoder this should be "4096". Nervertheless you can have a look at following FAQ: https://support.industry.siemens.com/cs/ww/en/view/84133347 Otherwise I think you should create a support request. Best regards TechSupport for SINAMICS S210 |