4/25/2016 1:42 PM | |
Joined: 4/25/2016 Last visit: 6/13/2024 Posts: 1 Rating: (0) |
Have you tried to look into PRODIX: https://workspace.ww007.siemens.net/content/00000457/Lopen/E-PRODIX/default.aspx ? There must be detailed manuals for FUM I/O modules. FUM 232 can handle up to 14 RTD's or 26 TC's. For RTD's connection 4 pins (two channels - each) are required (standard 4 wire RTD connection), for TC only 2 pins are required (one channel - each). For TC's handling FUM232 needs an external reference temperature measurement for "cold junction compensation", this measurement is supposed to be RTD and it has to be connected to the two first channels of the FUM232 Module (channel: 1&2 as 4 wire RTD). Hopefully it helps. |