3/8/2011 7:57 AM | |
Posts: 41 Rating:
|
Hi, Our IT department assigns IP addresses to all our hardware using a DHCP server. They will normally give me the subnet mask and IP address. This IP address is usually fixed for the MAC address but they can change it on their side if the wish. Is there any way to let the S7-1200 get its IP address automatically instead of specifying one? Worst case scenario if it is not possible to use the DHCP server, I will just have to get all the IPs for each PLC based on its MAC address and manually enter them. Thanks for any advice or help in advance! |
10/27/2011 5:03 PM | |
Posts: 126 Rating:
|
DHCP is not supported on the S7-1200 PLC. Currently it can be hardcoded, configured by T_CONFIG or downloaded by the Profinet DCP protocol. Sorry. John |
10/28/2011 11:01 AM | |
Posts: 41 Rating:
|
Thanks John. I am not familiar with the "T_CONFIG or downloaded by the Profinet DCP protocol" methods and I can't seem to find much info about them. Could you possibly shed some light on how I would go about using them. At the moment I am using the Primary Setup Tool and assigning IP addresses to the PLCs beforehand. Then in TIA Portal I select the "Set IP address using a different method" option when setting up the Profinet interface. This seems to work. |
8/15/2013 1:46 PM | |
Posts: 1 Rating:
|
We are in a similar situation. I would very much like to know how I can reliably change the IP address of my STEP 7 1200 PLC. Thanks! |
8/15/2013 6:16 PM | |
Posts: 1547 Rating:
|
Like from where, the PLC programm? Set the check for "Set IP address using a different method" Insert a T_CONFIG FB Call from Library > Communication > Open User Communication That's about it. |
10/20/2014 5:45 PM | |
Joined: 3/17/2014 Last visit: 8/31/2021 Posts: 31 Rating:
|
Hi, is this still that way? is DHCP not available for s7-1200? Thanks.
|
10/21/2014 11:31 AM | |
Posts: 1368 Rating:
|
jepp...still the same with S7-1200 CPUs... |
10/21/2014 11:50 AM | |
Joined: 3/17/2014 Last visit: 8/31/2021 Posts: 31 Rating:
|
Thanks for your help. I am wondering, is that something general an all PLCs or just the s7-1200? How is about s7-1500 or ET200? Cant find any information on their datasheets...
|
10/21/2014 12:16 PM | |
Posts: 1368 Rating:
|
plcs does not support this function. CPs I think supports DHCP |