Hi experts, As per the attached project, I am missing data for my detection and reaction components, but I can't see what's missing. I've tried searching for an explanation on the forums and the web, but haven't found anything definitive. Does anyone know what I'm missing? Thanks in advance! Attachmentprojects.zip (1012 Downloads) |
7/3/2018 9:56 AM | |
Joined: 6/11/2012 Last visit: 10/30/2019 Posts: 5 Rating:
|
Hi. CCF is below 65 points (currently 45 points for left/right pawl and 10 points for hydraulic valves) but shall be at least 65 points for cat2 - cat4 systems. Therefore you have to choose additional measures to avoid CCF (ISO 13489-1, Annex F). Best regards! |