12/11/2018 2:30 PM | |
Joined: 5/6/2010 Last visit: 6/2/2024 Posts: 1966 Rating: (274)
|
Hello, you should connect your signal between the isolator and the PLC to ground. regards
|
12/12/2018 7:36 AM | |
Joined: 5/6/2010 Last visit: 6/2/2024 Posts: 1966 Rating: (274)
|
Hello, if you have a lightning strike then you have a overvoltage at the input of your transducer. Your trancducer have a maximum voltage (normally up to 1..2 kV) to protect the input/output. If you need a lightning strike protection then you need additionally a surge protection like this Surge protection device - TTC-6P-1X2-F-M-24DC-PT-I
|
This contribution was helpful to1 thankful Users |