Hey, I use CPU414F-3PN controller and I have two g120 cu250s driver. The application is position control. I tried to use SINA_POS standart block in simatic manager but there is no any signal between cu250s and cpu. I checked sinapos block and I deleted optimize options but no any good new. IO start address is 528 and I wrote 210 as hexadecimal in Sinapos inputs. Normally, Many position control application that I had was with sinapos block but in Tia Portal. İs there any different things in Simatic Manager and Tia Portal about SinaPos? Can you help me? Thank you so much. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/15/2021 05:56:48New subject after splitting |
|
7/15/2021 5:58 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985) |
simple use the adress 528, have you try this? |
7/15/2021 2:01 PM | |
Joined: 4/6/2018 Last visit: 3/14/2024 Posts: 4 Rating: (0) |
I tried it ofcourse but no any answer from block. |
7/15/2021 2:12 PM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985) |
which telegram you use on the G120? |
7/15/2021 9:24 PM | |
Joined: 4/6/2018 Last visit: 3/14/2024 Posts: 4 Rating: (0) |
I use telegram 111(12word-12word) for position control. |