8/20/2019 5:02 PM | |
Joined: 4/13/2015 Last visit: 11/20/2022 Posts: 4 Rating: (0) |
Hi Sir; please I need support on the OP17 Error message I cannot Acknowledge the fault at OP 17 HMI panel The fault appearing "switch motor protection drive motor" and "switch motor protection vacuum pump" are already reset and digital input on PLC is available but still fault don't disappears appreciate technical advice sir ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/21/2019 09:12:42New subject after splitting |
|
8/21/2019 9:34 AM | |
Joined: 5/28/2008 Last visit: 5/26/2024 Posts: 4506 Rating: (836) |
Hello, Nobody can help without protool project downloaded to OP17 to get the trigger bit of this message, and also the PLC software and being online with PLC to monitor. Hope this helps. |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
8/23/2019 2:52 PM | |
Joined: 4/13/2015 Last visit: 11/20/2022 Posts: 4 Rating: (0) |
Thanks Sir Ayman, However, I prefer to take back-up from other OP 17 panel and restore it to this OP 17..Can this work? |
8/26/2019 9:07 AM | |
Joined: 5/28/2008 Last visit: 5/26/2024 Posts: 4506 Rating: (836) |
Hello, You have an alarm message and you don't know the reason or triggering condition. To know it you should monitor PLC after getting the triggering bit of this message. If you take a backup from OP17 and then restore same backup on the OP17 again, nothing will change. Because the problem that make this alarm message appears is still happening. Hope this helps. |
Ayman Elotaify |
|