4/11/2019 7:53 AM | |
Joined: 9/20/2014 Last visit: 2/7/2023 Posts: 56 Rating: (20) |
Hi all Dear I cannot go to Test Mode , i have error accordance with the attachment(Test mode error. Jpg). I compiled the program user again without problem but The problem(Test mode) did not resolve please help me about Resolve this problem Attachmenttest mode.pdf (564 Downloads) |
4/11/2019 4:30 PM | |
Joined: 8/31/2005 Last visit: 5/21/2024 Posts: 2197 Rating: (326)
|
Looks like you habe a FM458(-1). Is your PG/PC conneted to the FM or the S7-CPU? Serial port, MPI/PB or Ethernet? |
|
|
4/15/2019 6:17 AM | |
Joined: 8/25/2006 Last visit: 6/5/2024 Posts: 2206 Rating: (278)
|
Hello. Try the following actions via CFC-menu: 'CPU-Compare', 'CPU-Module Information' and 'CPU-Operating mode'. If you could get the results from these actions then your PG/PC Interface settings are correct. Try to download the program of FM458 with option 'Initial load'. |
4/16/2019 12:37 PM | |
Joined: 9/20/2014 Last visit: 2/7/2023 Posts: 56 Rating: (20) |
Hello I can't Access operating Mode from t CPU \ Operation mode(Ctrl I ) , but i have access to operation mode form HW config in online mode . I will try to check in the next few days option "Initial load" Thanks AttachmentFM458.pdf (732 Downloads) |
4/17/2019 9:57 AM | |
Joined: 9/20/2014 Last visit: 2/7/2023 Posts: 56 Rating: (20) |
yes , I tried "CPU-Compare" and "Module information " but I have Error 4305 (The communication link access the wrong module ). I will check at the first stop download the program of FM458 with option'Initial load'. Thanks |
4/22/2019 6:49 PM | |
Posts: 1 Rating: (0) |
where you able to fix the issue Error in The FM458 Test Mode ? If yes, please tell me how ? |
4/23/2019 12:40 PM | |
Joined: 9/20/2014 Last visit: 2/7/2023 Posts: 56 Rating: (20) |
Hi, The problem solved with download the program of FM458 with option'Initial load'. Thank for your help |
4/25/2019 11:45 AM | |
Joined: 9/20/2014 Last visit: 2/7/2023 Posts: 56 Rating: (20) |
|