3/28/2024 9:41 AM | |
Joined: 1/17/2013 Last visit: 5/25/2024 Posts: 1087 Rating: (6) |
Dear Technology Team, In the SINA-INFEED block how many input command should be "1" it have 2 command are EnablePrecharging and EnableInFeed which one should be "1" ? and what is the meaning each command ? What is the HWDSTW and HWDZSW ? Best Regards, ------------------------------------------------------------------------------------------ |
Last edited by: vorapob at: 03/28/2024 11:05:14Last edited by: Jen_Moderator at: 03/28/2024 13:16:15New subject after splitting Best Regards, |
4/2/2024 7:48 AM | |
Joined: 10/11/2006 Last visit: 5/23/2024 Posts: 5852 Rating: (793)
Dear vorapob, to enable your infeed please set the input "EnableInfeed" to TRUE. "EnablePrecharging" is only relevant for bigger infeeds. The Precharging process for Booksize devices is done internally. You can find this information in the manual of drive functionalities in chapter 3.1.4. https://support.industry.siemens.com/cs/de/en/view/109781535 HWIDSTW and HWIDZSW are the Hardware IDs of your configured Telegram 37x. You can find this information in the Hardware configuration of your S120 device in your TIA project. Please find detailled information of the function block interface in the manual in chapter 5.2.10 under the following link: https://support.industry.siemens.com/cs/de/en/view/109475044 |
Last edited by: Jen_Moderator at: 04/02/2024 11:38:44Links optimized. With best regards, |
This contribution was helpful to1 thankful Users |