Joined: 5/13/2008 Last visit: 12/18/2019 Posts: 836 Rating: (71) |
Hi, both, the TP170B as well as ProTool RT supports discrete alarms with message history. To do thisat the RT, there is nothing special to observe. Concerning the TP170B: - the message history is not battery-backed, you will lose all messages after rebooting the device. - the message buffersupports only up to 128 entries I would suggest you to use a CF card, for saving your messages using an archive. For this panel, siemens offered a CF card with 128 MB, item no. 6AV6 574-2AC00-2AA0 Hint: In the case of panels with Windows CE 3.0, you can theoretically use cards of up to 512 MB, not more! http://support.automation.siemens.com/WW/view/en/21847868 |
mfG / Best regards |
|
2/15/2010 9:52 AM | |
Joined: 4/24/2006 Last visit: 10/15/2024 Posts: 8745 Rating: (1168)
|
Hi, With the panel TP170B it is not possible to archive alarms. You can only use the message buffer, like earlier mentioned by The Body. The additional CF card is for Recipes or Project transfer. When you want to use Archives, you need at least an xP27x panel. Best regards, Wizard |