8/2/2010 12:13 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181)
|
Hello, First make backup of the existing project using Prosave. Then ESC+Arrow Rightt+ArrowDown (With this key combination, you erase the configuration memory when turning on the OP’s power supply). After ESC+Arrow Up (Loading of firmware and configuration is aborted and the system switches to Download mode). Cable and software is OK. Necessaries settings of PG com port: 1. Open Protool. Go to File->Download->Preferences. Select Serial, COM1, 38400; 2. Then File->Downlaad->Start Project Download. Into OP7 you must put it in Download Mode. Look upper or in OP7, OP17 Operator Panel Best regards, Hristo Mihalev |
8/3/2010 9:34 AM | |
Joined: 4/24/2006 Last visit: 5/31/2024 Posts: 8664 Rating: (1154)
|
Like already mentioned by UMENCHO: The combination ESC+right+down will erase panel. The combination ESC+Up will put panel in transfer mode without erasing project You should power off panel. Push the desired combination and hold them. Power on. Then you may release the buttons.
Have a look at this link: What connecting cables are there for connections between the operator panels and the different controllers? Search for 6XV1 440-2KH.. Best regards, Wizard |
Last edited by: Wizard at: 8/3/2010 9:36 AM |
|
8/3/2010 11:18 AM | |
Joined: 4/24/2006 Last visit: 5/31/2024 Posts: 8664 Rating: (1154)
|
You can use Protool/Pro Look at this link, for compatibility: Which version of SIMATIC ProTool/Lite, SIMATIC ProTool and SIMATIC ProT are compatible with which Windows Operating Systems? Best regards, Wizard |