3/8/2007 10:23 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (316)
Hi Hannibal, You need to place the HART-card in a ET 200M Station with a IM 153-2. If the Instrument is parametrized you don't need PDM, when not then you can get a demoversion to see what you can do, if that helps, you can buy the lowest amount of tags to program the equipment. PDM is to configure the equipment and testing it, after that you do not need PDM for the actual value. When the equipment is programmed then you can read out the analog value in the first word, the HART-value in the next 4 byte, then the status. See the handbook with the description of the 16 byte inputs of this card for the two channels. S7-300, ET 200M Automation Systems I/O Modules with Intrinsically-Safe Signals |