Hi Jose, well, you're right at this place. You should use FB72 (simplified communication), then you won't need further function blocks. FB72 will do the complete communication. In Spectation Communication Manual you can find a step by step description how to setup the simplified communication. If the communication works itself, don't forget to activate the inspection mode ("running man") in Spectation. Otherwise the camera will not transmit anything. Also, don't forget to setup a connection in VSLink PB (Cyclic Data In- and Out = 32 Bytes), even if you don't use the VSLink for visualization. http://support.automation.siemens.com/WW/view/en/27235703 Best regards RatedX |