Hello Usually there is a symbol showing AC or DC on the devices. Normally AC Coils should also carry the rated frequency e.g. 50 / 60 Hz. A Coil without the freq. specification is likely to be a DC Coil. For DC Coils, you can check the resistance with a Multimeter, it should be 24/1.61 ( Apprx 15 Ohms ) Ohms The attached application note may be of interest to understand the differences. Hope this helps Cheers Navnag AttachmentOperating_DC_Relasy_from_AC_and_Vice_Versa_13c3250.pdf (688 Downloads) |