9/18/2008 2:44 PM | |
Posts: 739 Rating: (55)
|
Hi Petrov82 Please have a look into the two links: http://support.automation.siemens.com/WW/view/en/31399077 http://support.automation.siemens.com/WW/view/en/10804985/133000 They might help you. |
9/19/2008 9:40 AM | |
Posts: 739 Rating: (55)
|
Hi Petrov82, please have a look into P0927 P0927 Specifies the interfaces which can be used to change parameters. This parameter allows the user to easily protect the inverter from unauthorized modification of parameters.Annotation: Parameter P0927 is not password protected. for a explanation of this parameter please have a look into the parameter list. http://support.automation.siemens.com/WW/view/de/23708204 I also suggest to do an Factory reset of your Inverter (P0970). Stop drive (i.e. disable all pulses) before you can reset parameters to default values. Set P0010 = 30 (factory settings). Set P0970 = 1 (resets all parameters to their default values). |
This contribution was helpful to2 thankful Users |
9/22/2008 8:55 AM | |
Posts: 7 Rating: (0) |
Thanks Jens S! OK, P0927 solve my problem!!! |