Hi, 02(dec) Read Input Status 03(dec) Read Holding Registers 04(dec) Read Input Registers 05(dec) Force Single Coil 06(dec) Preset Single Register 07(dec) Read Exception Status 08(dec) Loop Back Test 11(dec) Fetch Communications Event Counter 12(dec) Fetch Communications Event Log 15(dec) Force Multiple Coils 16(dec) Preset Multiple Registers
|
6/1/2010 4:23 PM | |
Joined: 10/7/2005 Last visit: 9/18/2024 Posts: 3021 Rating: (1054)
|
Hello timoreardon I'm afraid to say that I don't have good news for you as Function code 23 is definetly NOT supported by the CP341 Modbus Master. I must also say that I've never come across aModbus Slave which does NOT at least support FC 3 and 16. FC 3 and 16belong to ModbusConformance Class 0 (the lowest "common denominator" Modbus Conformace Class, this is the minimum useful set of functions, for both a Master anda Slave). Conformance Class 1 requires support for FC1, 2, 4, 5, 6 & 7. Conformance Class 2 covers 15, 20, 21, 22, 23 & 24 and typically found in HMI systems. As you see, the CP341 Modbus Master does fully cover Conformance Class 0 & 1 and a bit of CC2, so the question really is: Why does your Slave only support FC23? I'd put the hard word on the supplier of it and ask them to add at least CC0 compliance to it (i.e. FC3 & 16 support). Good luck and I hope this helps at least somewaht |