12/19/2013 5:45 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (708) |
Hi Eng. Mohamed, Have you already seen this manual? Takea look on chapter 5 ----> Migration from OP7 to OP77: SIMATIC HMI WinCC flexible 2008 WinCC flexible 2008 Migration Read page 126 The area indicators in ProTool are 4 bytes long. After migration, the area pointer is 10 bytes long. Successive area pointers may therefore overlap when you migrate the project. I think that you will need to change the length manually. |
Last edited by: Ste39 at: 12/19/2013 5:56 PM |
|
12/19/2013 6:26 PM | |
Posts: 784 Rating: (52) |
How? |
12/20/2013 9:39 AM | |
Posts: 784 Rating: (52) |
Hello Ste39, How can we change the lengh for area pointer in Wincc flexible program into 2 words?
|
12/21/2013 8:51 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (708) |
Hello Eng. Mohamed, sorry the delay, you can not "reduce" Area Pointer but create another. If your Area Pointer is a data block, it can increase by 5 Word for this Area Pointer. Please take a look: OP17 to OP177B Conversion issue |
12/23/2013 12:34 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, it iss not possible to switch between OP7 and OP77B without changes in the PLC-program. The structure of this area pointer is different. Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
This contribution was helpful to1 thankful Users |
Follow us on