8/29/2022 1:50 PM | |
Joined: 8/29/2022 Last visit: 8/30/2022 Posts: 2 Rating: (0) |
Hello, We are facing one problem in the Micro master 430 drive. Although we are setting the frequency to 50 Hz, it is not going beyond 39 Hz and the error A501 comes in. We tried doing it from BMS and also the keypad. But it gets stuck at 39Hz only. Kindly suggest the solution for the same. ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 08/31/2022 09:37:58New subject after splitting |
8/30/2022 4:25 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please check value set in p1082. It is for max frequency. If it is set to 39 then frequency above 39 Hz is not possible. P.S. - You have post this topic in wrong conference. You should have post it in MICROMASTER product conference. |
This contribution was helpful to1 thankful Users |