1/16/2011 11:45 PM | |
Joined: 6/4/2008 Last visit: 5/10/2024 Posts: 1484 Rating: (322)
|
Hi, is it possible that somebody has activated the the parameter lock, see the attached pages, P0011 - Lock P0012 - Key P0013 - List of 20 parameters that end user can access Using the AOP, you should be able to access the fault diagnostics directly. Regards, Graeme
AttachmentPages from Parameter List.pdf (129 Downloads) |
11/5/2011 12:37 PM | |
Posts: 2 Rating: (0) |
Dear Sir, I am having the same problem with my MM440. Checked all the connections. But problem not solved. Please help... |
11/7/2011 3:01 PM | |
Posts: 739 Rating: (55)
|
Drive is not in ready state (start inhibit) "OFF" commands have priority over "ON" commands. However, the converter requires a "Defined OFF command" which is defined only over OFF1 (normal ON / OFF). If an OFF2 or OFF3 is activated without OFF1, there is a "start inhibit" for "ON" (canceling of OFF2/3). AttachmentPages from 440_OPI_24294529_en_1006.pdf (141 Downloads) |
Last edited by: JensS at: 11/7/2011 3:03 PM |
|